Summary alert across a distributed system

Post by emaddocks »

Is there any plan in future OA versions to provide summary alerts across systems?

Currently it seems v3.18 does not allow this https://www.winccoa.com/documentation/W ... 0allowed).

It seems like something that should be possible as the DP list in the alert summary puts the system name prefix on the DP when you select it. It also doesn't raise a warning in the log viewer when you try. However when you raise the alarm on the other system the summary alert doesn't trigger.

User avatar
leoknipp
Posts: 2846
Joined: Tue Aug 24, 2010 7:28 pm

Re: Summary alert across a distributed system

Post by leoknipp »

It is not possible to use summary alerts with DP elements of distributed systems. Only datapoints of the own system can be used, even if the DP selector and/or the list of referenced elements shows the system name.

Best Regards
Leopold Knipp
Senior Support Specialist